DHB to run single solenoid

Includes expansion units, sensors, valves, wiring, communication cables etc.

DHB to run single solenoid

Postby Tulkas on Thu Mar 18, 2010 3:47 pm

Having problems trying to run a solenoid with the DHB.
Have got 1 PWM input from ECU and the one outlet to the solenoid.
The solenoid has two wires, one to ground the other from the DHB.

At the moment I am getting signal to the DHB but no response after that to the solenoid?

Regards
Tulkas
Tulkas
 
Posts: 1
Joined: Wed Mar 17, 2010 10:29 pm

Re: DHB to run single solenoid

Postby DarrenR on Mon Mar 29, 2010 2:29 pm

Hi Tulkas,

I'm not sure i fully understand how you have the DHB wired so i'll just go through how it needs to be.

See the data sheet here - http://motec.com.au/filedownload.php/CDS41213%20DHB%20Dual%20Half%20Bridge.pdf?docid=3244

The drawing at the bottom of the data sheet to drive two motors in a single direction is how you need to wire it.
Wire your solinoid in place of motor 1 in the drawing and leave the output pin to motor 2 disconnected.
You must wire both the power supply and ground wires as in the drawing, but you can have switched power if you want.
Your PWM signal from your ECU goes to input 1.

Hope that helps.
Darren Reynolds
MoTeC Research Centre - Melbourne, Australia.
DarrenR
MoTeC
 
Posts: 176
Joined: Thu May 01, 2008 2:15 pm
Location: Melbourne, Australia