Cold Junction compensations are performed using external sensors or the
E888 internal temperature sensor, according to the following rules:
• If only one of the two external cold junction compensation sensors (CJC1
or CJC2) is present then that sensor is used for compensations on all
thermocouple inputs.
• If both of the two external cold junction compensation sensors are present
then sensor CJC1 is used for compensations on TC1 to TC4, and sensor
CJC2 is used for compensations on TC5 to TC8.
• If neither of the two external cold junction compensation sensors are
present then the internal temperature sensor is used for compensations
on all thermocouple inputs.