C1812 does not display "Next Line" changes mode instead

D153, D175, C125, C127, C185 and C187 forum

C1812 does not display "Next Line" changes mode instead

Postby DynoDom on Tue Aug 29, 2023 6:11 am

Hello

As the title suggests, the M1 template comes with pin 53 configured to go to "Next Line".
Activating this function by connecting to sensor 0V changes mode instead. The same behavior
as pin 54 which is "Change Mode".

File attached.
Any help will be greatly appreciated. Thanks in advance.

D
Attachments
M1-template-nextlineprblem2.c1812v64
(1.35 MiB) Downloaded 365 times
DynoDom
 
Posts: 38
Joined: Wed Sep 14, 2022 12:10 am

Re: C1812 does not display "Next Line" changes mode instead

Postby Anthony on Wed Aug 30, 2023 1:37 am

By default you only need a single momentary button to perform both functions wired to pin 53

A short press of the next button will scroll to the next line.
A long press of the next button will scroll to the next page.
Any press of the mode button will scroll to the next page.

If you want to check the logic behind it you can goto calculations > user conditions.

If for some reason you do want them to be on seperate buttons you can give the attached file a go.
Attachments
M1-template-multi_button.c1812v64
(1.35 MiB) Downloaded 324 times
Anthony
 
Posts: 70
Joined: Fri Apr 19, 2019 12:54 am

Re: C1812 does not display "Next Line" changes mode instead

Postby DynoDom on Wed Aug 30, 2023 4:27 pm

Thank you very much Anthony.
D
DynoDom
 
Posts: 38
Joined: Wed Sep 14, 2022 12:10 am