Combine Outputs

PostPosted: Mon Jan 16, 2012 11:01 am
by Jakob
Hello,

is the reason why combining 8 A and 20 A outputs is not allowed, that the current will be shared equaly and then the 8 A outputs maybe get overloaded or are there other reasons?

If I want e.g. switch 32 A continuous and I've only one 20 A and three 8 A outputs left, can I combine this four outputs?

Thanks.

Jakob

Re: Combine Outputs

PostPosted: Tue Jan 17, 2012 11:24 am
by JamieA
The problem is that they will try to evenly share the load, so you will trip out the 8a output, when you go above 8a, leaving the 20a output running by itself...

You could either join all 3 8a outputs together, or use the 20.

I would suggest that you take one of your existing 8a outputs, and swap it for the 20a that you have spare.

you could then join the 4 8amp outputs together, giving you 32a total.

regards,

Jamie