PDM 30 Config Load Issue

Discussion and support for MoTeC Power Distribution Modules

PDM 30 Config Load Issue

Postby Enginetech on Wed Nov 10, 2010 6:10 pm

Has anyone had an issue with PDM not allowing changes to the operating file, then crashing the program? I am completely new to a PDM and this problem has stumped several US references. The scope of the problem is that the whole program reverts to something else, some base program, and won't allow us to operate any systems in the car. The last change is to try to pass the system check by assigning anything else to the output to clear the error message. I have tried 2 computers and cannot get past this issue. Would someone else attempt a chance to see if it is my programming deficiency or help me chase a product problem?
Attachments
SLEagle.pdm
(45.53 KiB) Downloaded 1195 times
Enginetech
 
Posts: 1
Joined: Tue Aug 05, 2008 5:47 pm
Location: Sparks, Nevada

Re: PDM 30 Config Load Issue

Postby NathanS on Fri Nov 12, 2010 7:34 am

This issue has been solved, it was a combination of incorrect output pin setup, the output channel that was being setup had been entered as the controlling channel for the output. This setup causes the software to crash when you click on OK in the output properties window.
NathanS
 
Posts: 53
Joined: Thu May 01, 2008 8:37 am


Return to PDM15 PDM16 PDM30 and PDM32